Thread: Caravan earth
View Single Post
Old Aug 27th, 2019, 13:31   #4
Tannaton
Bungling Amateur
 
Tannaton's Avatar
 

Last Online: Today 00:22
Join Date: Aug 2014
Location: Beverley, East Yorks
Default

Quote:
Originally Posted by luggsey View Post
Be careful with RCDs on inverters, some inverters run two phases of 110v making 230 across phases, this works most domestic electrical appliances and lights without problem.
Your RCD may require 230v on the phase to work correctly, only way to be sure is to use an RCD tester when the installation is running on invertor.
Similarly your overload device needs to disconnect at below peak current of the inverter, otherwise a fault may not pull the mcb...
Some use an earth stake with a generator but I don't think there would be any reason to in your case.
It's a can of worms using mains/inverters on mobiles!
Would agree with most of the post but would make the following points:

- Pure Sine Wave inverters (which the OP is using) are usually of much higher quality than modified sine wave inverters and I've yet to come accross one that works in "anti-phase" as you describe, so they should be okay with RCD's, but as you say best to test.

- Ground Earthing spikes for generators are usually used when domestic wiring is connected to them (i.e. building or portacabin) and is there for equipotential bonding.
__________________
2011 XC90 D5 Executive
2003 C70 T5 GT
2012 Ford Ranger XL SC
1977 Triumph Spitfire 1500
1976 Massey Ferguson 135
Tannaton is offline   Reply With Quote